Modbus settings
If the ventilation unit is connected to e.g. a building automation system via Modbus, configure the Modbus settings. The Modbus settings are:
- Ventilation unit’s Modbus address
- Modbus baud rate
- Modbus parity
- Modbus stop bit.
To configure the Modbus settings:
- Select Settings.
- Select Expert settings with the arrow buttons.

- Select OK.
- Select I/O and bus settings with the arrow buttons.

- Select Modbus settings with the arrow buttons:

- Select OK.

The Modbus 1/4 screen opens.

- Use the Plus and Minus buttons to set the ventilation unit’s Modbus address. You can set the address between 1 and 247.
- Select Right arrow.
The Modbus 2/4 screen opens.

- Use the Plus and Minus buttons to set the Modbus Baud rate. The options are 9600, 19200, 38400, 57600 and 115200.
- Select Right arrow.
- The Modbus 3/4 screen opens.

- Use the Up arrow and Down arrow buttons to set the Modbus Parity. The options are:
no — No parity
even — Even parity
odd — Odd parity.
- Select Right arrow.
The Modbus 4/4 screen opens.

- Use the Plus and Minus buttons to set the Modbus Stop bit. The options are 1 or 2.
- Select OK.