Sound values

Table 1. Sound power level in the supply air duct
Sound power level in the supply air duct (one duct) by octave band L dB
Adjustment position (%) 10 20 30 40 50 60 70 80 90 100
Medium frequency of the octave band Hz 63 57666669737577798082
125 43525764666971727373
250 41465055596474727375
500 35414852555861646768
1000 30384348525558616465
2000 24334146505456596163
4000 17202734404549525557
8000 21212225313742464952

L dB

58666670747780808284

LWA´ dB(A)

38455055596268687072
Table 2. Sound power level in the extract air duct
Sound power level in the extract air duct (one duct) by octave band L dB
Adjustment position (%) 10 20 30 40 50 60 70 80 90 100
Medium frequency of the octave band Hz 63 50515559646568727676
125 38485053545557575959
250 33394548526063636464
500 24303639424649505253
1000 18263136394345485051
2000 13182530353841444647
4000 17171820242932353839
8000 21212121212223252830

L dB

50535661656770737777

LWA´ dB(A)

30364044485356575959
Table 3. Sound pressure level coming through the envelope
Sound pressure level coming through the envelope of the unit in the room in which it is installed (10 m2 sound absorption)
Adjustment position (%) 10 20 30 40 50 60 70 80 90 100
LpA, dB (A) 24262934394144474949

You can calculate the sound values for each operating point with the Vallox MySelecta control panel.