Sound values

Table 1. Sound power level in the supply air duct

Sound power level in the supply air duct (one duct) by octave band Lw, dB

Adjustment position

Adjustment position (%)1020304050607080100
Air flow dm3/s152434425162697783
Air flow m3/h5486122151184223248277299
Medium frequency of the octave band Hz63626469737782848788
125536365656771747678
250485660657071737575
500434956606467697173
1000354349535661646567
2000253644495256586162
4000182332384348515455
8000212229374349525557
LW, dB636771747883858888
LWA, dB (A)435357616568717274
Table 2. Sound power level in the extract air duct

Sound power level in the extract air duct (one duct) by octave band Lw, dB

Adjustment position

Adjustment position (%)1020304050607080100
Air flow dm3/s233141506070788692
Air flow m3/h83112148180216252281310331
Medium frequency of the octave band Hz63545562666975787980
125465053565962656768
250394551556059616264
500293540444750555456
1000162430343740434646
2000131723283236384142
4000171718202428303335
8000212121212223252829
LW, dB545763667075787980
LWA, dB (A)354045495355585960
Table 3. Sound pressure level (A)
Sound pressure level coming through the envelope of the unit in the room in which it is installed (10 m2 sound absorption) Adjustment position / Air flows (supply/extract)
Adjustment position (%)1020304050607080100
Air flow dm3/s15/2024/3033/4042/4852/5861/6870/7678/8483/89
Air flow m3/h54/7286/108119/144151/173187/209220/245252/274281/302299/320
LpA, dB (A)222732353843444647

You can calculate the sound values for each operating point with the Vallox MySelecta control panel.