Table 1. Sound power level in the supply air duct| Sound power level in the supply air duct (one duct) by octave band LW´ dB |
|---|
| Adjustment position (%)
| 10
| 20
| 30
| 40
| 50
| 60
| 70
| 80
| 100
|
| Air flow (dm3/s)
| 6 | 10 | 17 | 21 | 26 | 32 | 35 | 40 | 44 |
| Medium frequency of the octave band Hz
| 63
| 59 | 66 | 70 | 72 | 74 | 79 | 78 | 79 | 81 |
| 125
| 57 | 62 | 64 | 66 | 69 | 71 | 73 | 76 | 76 |
| 250
| 47 | 55 | 62 | 66 | 68 | 69 | 71 | 73 | 73 |
| 500
| 36 | 44 | 50 | 55 | 59 | 63 | 66 | 68 | 70 |
| 1000
| 29 | 39 | 45 | 50 | 54 | 59 | 61 | 63 | 65 |
| 2000
| 21 | 29 | 39 | 45 | 50 | 53 | 56 | 58 | 60 |
| 4000
| 18 | 19 | 24 | 32 | 40 | 46 | 50 | 53 | 55 |
| 8000
| 21 | 21 | 22 | 23 | 26 | 31 | 36 | 40 | 43 |
| LW, dB
| 62 | 67 | 71 | 74 | 76 | 80 | 80 | 81 | 83 |
| LWA, dB(A)
| 44 | 51 | 56 | 60 | 63 | 66 | 68 | 72 | 72 |
Table 2. Sound power level in the extract air duct| Sound power level in the extract air duct (one duct) by octave band LW´ dB |
|---|
| Adjustment position (%)
| 10
| 20
| 30
| 40
| 50
| 60
| 70
| 80
| 100
|
| Air flow (dm3/s)
| 7 | 14 | 22 | 24 | 30 | 35 | 40 | 45 | 48 |
| Medium frequency of the octave band Hz
| 63
| 55 | 59 | 61 | 64 | 67 | 76 | 72 | 72 | 73 |
| 125
| 57 | 60 | 62 | 66 | 68 | 70 | 72 | 74 | 77 |
| 250
| 39 | 47 | 55 | 60 | 61 | 62 | 63 | 65 | 67 |
| 500
| 26 | 33 | 38 | 42 | 47 | 52 | 55 | 57 | 57 |
| 1000
| 21 | 29 | 34 | 38 | 42 | 45 | 48 | 50 | 52 |
| 2000
| 13 | 15 | 22 | 27 | 32 | 35 | 37 | 39 | 41 |
| 4000
| 17 | 17 | 18 | 18 | 21 | 25 | 28 | 32 | 34 |
| 8000
| 21 | 22 | 21 | 21 | 22 | 22 | 22 | 22 | 23 |
| LW, dB
| 59 | 62 | 65 | 69 | 71 | 77 | 75 | 77 | 79 |
| LWA, dB(A)
| 41 | 45 | 50 | 54 | 56 | 58 | 60 | 62 | 64 |
Table 3. Sound pressure level in the room| Sound pressure level coming through the envelope of the unit in the room in which it is installed (10 m2 sound absorption) |
|---|
| Adjustment position (%)
| 10
| 20
| 30
| 40
| 50
| 60
| 70
| 80
| 100
|
| Air flow dm3/s (supply/extract) | 6/7 | 12/14 | 19/22 | 22/25 | 27/30 | 31/34 | 35/40 | 41/45 | 44/48 |
| LpA, dB (A)
| 24 | 29 | 35 | 38 | 40 | 45 | 47 | 49 | 50 |
You can calculate the sound values for each operating point with the Vallox MySelecta control panel.