Table 1. Sound power level in the supply air duct| Sound power level in the supply air duct (one duct) by octave band LW´ dB |
|---|
|
Adjustment position (%)
|
10
|
20
|
30
|
40
|
50
|
60
|
70
|
80
|
100
|
|
Medium frequency of the octave band Hz
|
63
| 84 | 84 | 81 | 80 | 70 | 73 | 73 | 68 | 61 |
|
125
| 81 | 80 | 74 | 72 | 71 | 68 | 65 | 64 | 57 |
|
250
| 74 | 74 | 73 | 71 | 69 | 67 | 65 | 71 | 57 |
|
500
| 76 | 75 | 70 | 64 | 62 | 60 | 63 | 58 | 43 |
|
1000
| 70 | 70 | 67 | 67 | 64 | 61 | 58 | 54 | 43 |
|
2000
| 64 | 64 | 62 | 59 | 57 | 54 | 51 | 47 | 33 |
|
4000
| 59 | 59 | 57 | 55 | 53 | 49 | 45 | 40 | 23 |
|
8000
| 55 | 55 | 53 | 50 | 47 | 43 | 38 | 32 | 21 |
|
LW, dB
| 87 | 86 | 82 | 81 | 181 | 76 | 75 | 73 | 64 |
|
LWA, dB(A)
| 76 | 75 | 72 | 70 | 68 | 65 | 64 | 64 | 51 |
Table 2. Sound power level in the extract air duct| Sound power level in the extract air duct (one duct) by octave band LW´ dB |
|---|
|
Adjustment position (%)
|
10
|
20
|
30
|
40
|
50
|
60
|
70
|
80
|
100
|
|
Medium frequency of the octave band Hz
|
63
| 82 | 82 | 81 | 79 | 78 | 74 | 69 | 66 | 56 |
|
125
| 78 | 78 | 72 | 69 | 67 | 64 | 62 | 58 | 48 |
|
250
| 68 | 68 | 67 | 66 | 65 | 61 | 58 | 55 | 46 |
|
500
| 56 | 56 | 54 | 52 | 56 | 49 | 46 | 43 | 30 |
|
1000
| 50 | 50 | 48 | 47 | 45 | 42 | 39 | 35 | 24 |
|
2000
| 44 | 44 | 43 | 41 | 39 | 35 | 32 | 27 | 16 |
|
4000
| 37 | 37 | 36 | 34 | 31 | 28 | 24 | 20 | 16 |
|
8000
| 32 | 32 | 30 | 28 | 25 | 23 | 21 | 20 | 20 |
|
LW, dB
| 84 | 83 | 82 | 80 | 78 | 75 | 50 | 67 | 57 |
|
LWA, dB(A)
| 65 | 65 | 62 | 60 | 59 | 56 | 53 | 49 | 40 |
Sound pressure level coming through the envelope of the unit in the room in which it is installed (10m² sound absorption)
|
|---|
| Adjustment position (%) | 10 | 20 | 30 | 40 | 50 | 60 | 70 | 80 | 100 |
| LpA, dB (A) | 26 | 30 | 36 | 41 | 43 | 44 | 45 | 47 | 47 |
You can calculate the sound values for each operating point with the Vallox MySelecta control panel.