Sound values

Table 1. Sound power level in the supply air duct
Sound power level in the supply air duct by octave band LW´ dB
Adjustment position (%) 10 20 30 40 50 60 70 80 90 100
Air flow (dm3/s) 15 20 32 37 47 57 62 65
Medium frequency of the octave band Hz 63 60 67 68 72 73 79 79 78
125 56 65 64 66 68 70 72 73
250 51 58 67 70 74 78 76 76
500 41 49 55 59 63 66 70 70
1000 39 47 52 55 58 62 65 66
2000 30 41 48 52 56 59 62 62
4000 19 28 36 42 46 51 54 55
8000 21 22 28 35 42 48 52 53
LW, dB 61 70 72 75 77 82 82 81
LWA, dB(A) 46 55 61 64 68 72 72 75
Table 2. Sound power level in the extract air duct
Sound power level in the extract air duct by octave band LW´ dB
Adjustment position (%) 10 20 30 40 50 60 70 80 90 100
Air flow (dm3/s) 17 22 36 42 51 60 66 67
Medium frequency of the octave band Hz 63 54 58 59 63 66 78 70 73
125 48 56 54 56 58 62 63 64
250 43 50 61 59 61 63 65 64
500 30 37 43 46 49 53 60 60
1000 27 35 39 43 46 50 52 53
2000 15 23 29 33 37 40 42 43
4000 17 17 18 21 25 29 31 32
8000 21 21 21 21 22 23 25 26
LW, dB 55 61 64 65 68 78 72 74
LWA, dB(A) 38 45 53 52 54 58 61 61
Table 3. Sound pressure level in the room
Sound pressure level coming through the envelope of the unit in the room in which it is installed (10m² sound absorption)
Adjustment position (%) 10 20 30 40 50 60 70 80 90 100
Air flow (dm3/s) 15/17 33/39 32/36 38/42 47/51 19/20 62/67 65/67
LpA, dB (A) 26.9 33.2 40 43.1 46.3 49.7 51.5 52.1