Duct radiator control
The duct radiator can be located either in the outdoor or the supply air duct. If the radiator is installed in the outdoor air duct, it can be used for both preheating and cooling, or for preheating or cooling alone. If the duct radiator is installed in the supply air duct, it can be used for cooling only.
The duct radiator can be set to function either automatically or manually:
- Automatic — In summer, the supply air temperature will be maintained at the level specified in the temperature setting. In winter, the duct radiator will turn on, when the outdoor temperature falls below the winter setting.
- Manual — In summer, the duct radiator will turn on, when the outdoor temperature rises above the summer setting. In winter, the duct radiator will turn on, when the outdoor temperature falls below the winter setting.
- Automatic — The supply air limit is adjusted automatically based on the dew point of the extract air. When the supply air temperature falls too low, the duct radiator will turn off.
- Manual — The supply air limit can be set manually. When the supply air temperature falls down to the set value, the duct radiator will turn off.
Please observe the risk of condensation when making changes to duct radiator settings.
- Select Settings.
-
Use the Arrow buttons to select Expert settings.
- Select OK.
-
Use the Arrow buttons to select I/O and bus settings.
- Select OK.
-
Use the Arrow buttons to select Relay settings.
-
Select OK.
The Relay settings display opens.
-
Use the arrow buttons to select Duct radiator control as the operating method of the relay.
The Duct radiator settings display opens.
-
Use the arrow buttons to set the operation of the duct radiator. The options are:
- Automatic
- Manual
- Select Right arrow.
-
Use the Plus and Minus buttons to set the summer setting.
Note:
If the operating method of the duct radiator is set to automatic, the summer setting cannot be changed. The adjustment range of the summer setting is +10 °C - +25 °C. The factory setting is +15°C.
- Select Right arrow.
-
Use the Plus and Minus buttons to set the winter setting. The adjustment range of the winter setting is -10 °C - +5 °C. The factory setting is -5°C.
- Select Right arrow.
-
Use the arrow buttons to select the method of use of the duct radiator.
The options are:
- Both — The duct radiator is used for preheating and cooling.
- Pre-heating — The duct radiator is only used for preheating.
- Cooling — The duct radiator is only used for cooling.
- Select Right arrow.
-
Use the arrow buttons to select the adjustment method of the supply air limit. The options are:
- Automatic — The supply air limit is adjusted automatically based on the dew point of the extract air.
- Manual — The supply air limit can be set manually.
- Select Right arrow.
-
Use the arrow buttons to select the adjustment of the supply air limit. The adjustment range of the supply air limit is +12 °C - +25 °C.
Note:
If the supply air limit is set to automatic, the supply air limit cannot be adjusted manually.
- Select Right arrow.
-
The External sensor settings display opens.
Use the arrow buttons to select the method of use of the external sensor. The options are:
- Not in use — The duct radiator is located in the outdoor air duct, no external sensor has been connected.
- Control of outdoor air duct radiator — The duct radiator and the external sensor are located in the outdoor air duct.
- Air heating control — Not used in the controlling of the duct radiator.
- Supply air duct radiator control — The duct radiator and the external sensor are located in the supply air duct.